This forum makes use of cookies to store your login information if you are registered, and your last visit if you are not. Cookies are small text documents stored on your computer; the cookies set by this forum can only be used on this website and pose no security risk. Cookies on this forum also track the specific topics you have read and when you last read them. Please confirm whether you accept or reject these cookies being set.

A cookie will be stored in your browser regardless of choice to prevent you being asked this question again. You will be able to change your cookie settings at any time using the link in the footer.

Thread Rating:
  • 1 Vote(s) - 5 Average
  • 1
  • 2
  • 3
  • 4
  • 5
How do I pipe temp data from 1W to kplex for distribution as NMEA0183
#21
(2018-07-15, 08:15 PM)e-sailing Wrote: All things are correct 24.81 K is -248.3 C  (24.81-273.15).
Signalk uses only SI units!!! But you generated a signalk value with C (SI unit for temperature is K).
The diag has a selection private Unit. This converts signalk values to readable units only for diag! Switch it off. Now look if the value is correct (it isn't and you will see that bme value is (273.15+26.19)).

The temperature value you send with mqtt must be in Kelvin.
Thanks.
changed mqtt to send in K works now, any way to display in fahrenheit.?
i looked on cruisers forum there was a post about that 5 yrs ago with no response Sad
http://www.cruisersforum.com/forums/show...ost2674322
Reply


Messages In This Thread
RE: How do I pipe temp data from 1W to kplex for distribution as NMEA0183 - by jim321 - 2018-07-16, 09:19 AM